how to check the continuity of a cable with a megger
Answer Posted / sanjayjssate
its very simple
Connect the other ends of cable togather and take megger from other end at very low voltage, if megger is zero means it is continuty is one, again seprate the the cable and take the megger if megger is more tha 100 Kohm, means cable is healthy.
| Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
what is parellel power factor correction?
How to calculate LT XLPE CABLE for 11 kv / 433 v , 1000 kva oil type transformer system?
What determines the thickness of the lamination or stamping?
how could we know the size of cable by physical view?
HOW TO CALCULATE THE HEAT AND LOAD OF LT-SUBSTATION WHICH CONTAINS 2*1MVA TRANSFORMERS,LT-SWITCH BOARD,MLDB,ACB,BUSBAR,ETC,......?
why HT armoured cable does not glanding
why all the feeders are designed in a particular manner ... is there any reason for that???
What is the formula to calculate the no load current of a single & three phase induction motor
Differentiate between Zero and Negative sequence current
what is the meaning of number in (11, 31, 61,14, etc. CDG11, CDG31, CDG61, DDT32
bitumar
How can we calculate the KVA rating of a Distribution transformer from its core details?
we can run 2phase as 3phase .what will be the differnce with respect to phase angle, power, current between the two modes
If any one's require of phoenix contact like( relay , termilnal block , surge protection device ) , product please contect me 09878206357 chetan verma
what is the difference between ups & inverter