In dcs contol valve parameters showing like this
Gain=1 or 2 , ti=7 sec, td=20sec. But temp,pressure,level control valves we are using in which type parameter side using ti,td clearly tell me
Answer Posted / carl_ellis
Gain, ti and td are PID proportional control tuning terms/constants. PID controllers use PID tuning constants to calculate an output based on the error signal; final control elements (valves) do not do a PID calculation so valves are not involved with gain, ti and td. The controller is typically in the control room, the valve is somewhere out in the process.
A PID controller calculates the expected valve/damper position from the error signal and the tuning constants, the result of which is an output control signal ranging from 0-100%.
A valve positioner or valve I/P receives that control signal from a controller (4-20mA, Profibus) and supplies air or electric power to the actuator to achieve the correct position demanded by the control signal.
Ti is the term for reset or integration. It is used when the process itself is not an integrating process. Level, pressure, and pH are usually integrating processes. Sometimes temperature is an integrating process, sometimes not. When the process is non-self regulating/integrating process, the ti term is not used in the PID calculation.
Flow and temperature processes typically use the ti term for PID calculation.
An exception to the rule of PID being done in a separate controller is Foundation Fieldbus (FF), which allows function block PID execution in FF devices. In a case where PID control is executed in an FF valve positioner, then a valve would use the PID tuning constants.
Is This Answer Correct ? | 4 Yes | 0 No |
Post New Answer View All Answers
How to decrease opening & closing time of on/off valve?
what is effect of specific gravity in differential level transmitter , explain formula related with this .
I m appointed as an automation trainee engineer in small firm in that I am only the one , my company give me a project on s7-200 as i m beginner I don't know how to program so please send me the helpful site so that I complete my project before deadline....please help me out in this critical situation.
How do you identify an orifice in the pipeline?
How can measure flow in oil line?which type of transmitter is generally used?
What is modbus?
How to interfacing microcontroller with a DC motor
the 3 most common transmitter protocol being in refinery or qatar gas and aramco.
we are using centum vp as monitoring with Dell precision work station T3600 but some times PC(s) are restarted automatically . how we can solve this problem? thanks
Hi Friends i am going to write BARC written test by this month 20th (20-5-2008). So please if any body knows the details about this or having previous question papers pls mail me to kkumarei@gmail.com. For Suggestions give one message to 9962122264
Can any one tell me what type of question asked for instrumentation and control interview panel??? pls mail ramashankar.goel@gmail.com
How servomotor controls throttle valve of TURBINE?
i hav applied for the post of engg. in iocl so please require the past test papers fro instrumentation engg please please help me and send me the papers or tell me the pattern and type of ques asked in examination......
can you provide me full detail about instrumentation in ONGC??
How is automatic reference junction compensation carried out in temperature recorders?