What is the Difference Between MCCB & ACB & VCB
Answer Posted / md.yeasir arafat
MCCB : Molded Case Circuit Breakter.
Range : Up to 1600A, 3pole and 4pole , in fixed, plug in and draw out version.
Breaking Capacity : Up to 70KA (Higher breaking capacity also available).
Application : Protection of line, transformers and motors.
ACB : Air Circuit Breaker.
Range :' 800A to 6300A.
Application : Incoming and outgoing circuit breakers in distribution systems, switching and protection of motors and generators.
VCB : Vacuum Circuit Breaker
Rated Voltage : 15KV
Normal Current : 2000A
Short Circuit Breaking Current : 31.5KA
Rated Voltage : 24KV
Normal Current : 1250A
Short Circuit Breaking Current : 25KA
Rated Voltage : 36KV
Normal Current : 4000A
Short Circuit Breaking Current : 40KA
| Is This Answer Correct ? | 2 Yes | 0 No |
Post New Answer View All Answers
Percentage losses in power generation?
why we use ac supply as 415 volts instead of 415 v why we cant apply 230 v for dc
what r substations?what r there work?why voltages r incresed and then reduced during distribution of power
What is the name of transformers oil filteration equipment?
What's mean HVF & HAF in Vacuum Circuit Breaker?
HOW DO YOU CAN CHECK A 15KV DIODE, WHETHER IT IS OK OR NOT?
Whether the vacuum contactor requires Short circuit protection?If No,why?
Define what is difference between fuse and breaker?
how is calculated the quantity of weight in hot test xlpe?
why we have and use 3 phase not 2 or 4 or other in power system?
what is meant by carrier aided trip protection in transmission line
it is possible to rotate the DG engine dc starter with wrong polarity connections? why?
i want design of D.C.MOTOR 1HP 960RPM AND 2HP 960RPM ITS URRGENT
What is the effect on 3phase induction motor if current setting knob of DOL kept at minimum current?
how make megger test for control cable like 12c x 1.5mm and what it apply voltage and test timing details.