what will be happened when a single phase motor is supplied
by the dc supply
Answer Posted / alan jenkins
In a nutshell it depends what type of motor it is, some motors with a wound rotor and brushgear will run on AC and DC, however AC induction motors will not rotate, the DC current will have a locking effect on the rotor, hence DC injection braking (anyone heard of that ?)leaving a DC current on these motors for any length of time will heat up the windings.
Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
Difference between rating factor of cable and derating factor of cable?
placing earthing pit in pathway is correct or wrong??. placing earthing wireGI1/18 inside walls is correct or wrong?. explain!!!
what is the criteria for selection of conductor used for ehv ac electrical dischrge
To prove the capacity of a 10MVA transforemr with 6.5% impedance by a short circuit test how much power is needed to inject an impedance voltage if we have to arrive for its rated current?
Why Neutral Isolation is required?
what is the sludge current
diff b/w elcb and rccb
What is class ab operation?
describe the Tranformer testing procedure
What are the basic elements used for modeling mechanical rotational system?
A jet of fluid strikes a plate What was the force required to counter it?
what is formula to cal cute earth pit numbers and size of earth strip used in earthing?
What is quadrantal symmetry?
I have a CT meter with ratio 60/5. The meter reading of previous month was 3290.49 and that of current month was 3797.26. How many chargeable units as per normal meter should be my reading.
what is the use of power transformer in GSS.