what is the formula to find out how many amps generater
takes running on full load.
Answer Posted / k.gurusamy
P=√3*V*I*0.8
P in KW
V=415V
I=?
ANS:
P=1.732*415*I*0.8
KW =575.024*I
KW/575.024=I
I=(0.00174*KW) AMPERE
| Is This Answer Correct ? | 0 Yes | 0 No |