what is RTD? what is THERMOCOUPLE? What is difference between
it?
Answer Posted / tamjid
RTD is cheaper than thermocouple, and TC is more accurate than RTD, we use RTD for temp sensing bello 150C, but TC used for high temp sensing,
| Is This Answer Correct ? | 1 Yes | 0 No |
Post New Answer View All Answers
An active element is one which a. Supplies energy b. Absorbs energy c. Supplies energy and convert energy from one form to another
During Testing of Maintenance Free Earthing, How deep should be the Spikes of Earth Test Meter should be inserted in the soil(one spike is 15 Meter & Other spike is 30 Mtrs away from the Main Earth Electrode. Because, recently, we observed that when spike is inserted 3-4 Inch in the earth- results are better, If spike is inserted 1 feet deep than results are increasing.
How much minimum insulation required between 11kv/3.3kv transformer windings?
What is the meaning of loop in transformer
What is error of a measurement?
How to calculate main incomer rating of APFC Panel ? Let's say i want to find main incomer for 11kV, 1000kVAR Panel.
which VFD is better ( LT or HT)
when the time of backcharging the transformer three phases only enough or three phase with neutral is must.from these which one is the best one.
What is servo motor? what is its purpose?
HOW WE CAN REDUCE THE CIRCUIT COMPLEX OF STAR-DELTA STARTER .BECAUSE NOW WE USING ONE TIMER RELAY & THREE CONTACTOR FOR MAIN,STAR & DELTA ?IF ANY IDEAS PLZ POST.THANK U
WHAT IS THE DIFFERENE IN ACTION OF MCB,MCCB,RCCB
If I have Energy Meter Ratio as 100:5 & Also I have CT Ratio as 50:5 then what will be my multiplying Factor(M.F.)
Whether 3 phase induction motorwith 100 hp capacity , Amp 160 for which sensitive earth fault relay , type CTUM 15 can be used?
In radial network the source is fed from 1 end both ends at central
Why Stabilising Resistor used in REF circuit ?