What is Hysteresis mean in Instrument?

Answer Posted / zaiwar ali

when we increase the input of an instrument it gives some
output readings (follow a curve), now if we decrease the
same input and it gives different readings (follow another
curve) then this effect of instrument is called hysteresis.

Is This Answer Correct ?    66 Yes 7 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

How can a d.p. Transmitter be calibrated?

682


What is cut off relay? And why use in PLC and DCS?

940


Draw symbols of the following :

1527


what are the documents(Construction point of view for a process plant) submitted by contactor initially entering in to new site for client?

1754


How you calibrate absolute pressure with the calibration range of 0 to 1000 0C Absolute. Please explain the procedure for calibration.

1275






Make a ladder diagram on LSL valve will close, on PSL valve will open and start the motor

1679


what should he know if he is an assitent engineer instrumentation in cement industries of experience of 10 - 15 year.

1619


How to Calibrate Temperature Switch in field

798


Name different types of bourdon tubes.

669


how to connect transmitter measuring sulfur process? 1-by using long impulse line or 2- by using coated short impulse line

1579


what is the responsibility of an instrument commissioning supervisor

2638


How many interlocks at turbine side?

1436


how to commission furnace ( water heater)

1500


I have 0.75mm sq multicore cable (IS type) , can use instead of same type but 1.5 sq mm cable ? Note : The distance is around about 150 meter.

1158


what is different between 2,3&4 wire rtd and how much maximum distance using plc to field.

2276