How to calculate rated currennt Of Mcb for 2hp motor...
Answer Posted / shri..
v = 415
hp = 2
PF 0.7
W = 1492
A = (1492)/(415*1.732*0.7)
A = 1044.4 /503.14
A = 2.96 Amps / Phase
Take a MCB c curve type
Is This Answer Correct ? | 16 Yes | 3 No |
Post New Answer View All Answers
Differentiate between magnetic field and magnetic flux?
Why i receive the GCU fault in my DG Sychronization panel . what all the factors considered for this fault .
typically in power distribution substation. 1- Any idea how would be the graph of capacitor bank consumption verses time through the day . 2- How is the switching ( on and off ) of the capacitor bank, per need?
how is the cable tray designed & how its total length is calculated for an Industrial plant Say for Ex. (500KW Motor Load)
i want bhel placement paper for electrical if anybody having pl send to my id kavitha867@myway.com immediately
Any one who apply for Ferro Scrap Nigam Limited cn join with me at rajuhalder@indiatimes.com or 09669717028
What is difference between safe PLC and normal PLC
How can we increase fuel-power ratio of any DG set?
how ceiling fan worked?
how to calculate the power factor when instantaneous voltage and current has harmonics in it ?
Differentiate between ideal and non-ideal voltage sources?
Can anybody tell abt concrete encased earthing or grounding?
hi guys please tell me the procedure for mesuring the coil resistance of 3ph induction motor?
How much earthing frequency is capable?
why 5kW motor becomes unbalance if its relay trip 1st time and its set value is 7.0 A