How to calculate rated currennt Of Mcb for 2hp motor...
Answer Posted / shri..
v = 415
hp = 2
PF 0.7
W = 1492
A = (1492)/(415*1.732*0.7)
A = 1044.4 /503.14
A = 2.96 Amps / Phase
Take a MCB c curve type
| Is This Answer Correct ? | 16 Yes | 3 No |
Post New Answer View All Answers
how to changeover ups in this power failur time?
what is the chiller and working principal
Why we do 2 types of earthing on transformer (ie:)body earthing & neutral earthing , what is function. I am going to install a oo kva transformer & 380 kva dg set what should the earthing value?
what is the safety points of vaccum circuit breaker.
A 100W electric lamp is supplied from a 115V, 60HZ source. The peak instantaneous power dissipated in the lamp filament is
What is the fault or needs to be done when frequency in ac drives is not changing?
33kv Rated output avilable in market (any where in india)
Basic motor transformer generator
What do you understand by oldham's coupling ?
how to find motors H.P. whout any rating? (only give you a motor and multimeter)
how to select correct size of power cable for inverter duty motor
sent to a site and asked to explain how you would like a twenty seven flour building should be supplied with lighting and sockets plus a water boiler.
what will happen if ac and dc supplies given
Is RTCC panel needs any control supply.
Please tell me in DETAIL about the following 3 types of fuses or recommend me a good power system protection book or a website link ? 1.Dropout Fuse 2.Striker Fuse 3.Empulsive fuse (not sure if its impulsive or explosion fuse , sorry)