Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

the inertia constants of two machines are respectively 30and
42 MJ per MVA.when the change in frequency due to change in
load in first machine is 12 Hz,the change in second machine
frequency will be?

Answer Posted / 7anoter4

If the change in load will be the same Pa1=Pa2 and the
rated frequency fo1=fo2

for the same time interval dt1=dt2

IF Pa=H*MVA/180/fo*d2&#61540;R/dt2 [See IEEE-399 ch. 8.6.2 How
stability programs work]

and d2&#61540;R/dt2=2*pi()*df/dt

then (df/dt)1=Pa/2/pi()*180*fo/MVA1/H1 and

(df/dt)2=Pa/2/pi()*180*fo/MVA2/H2

(df/dt)2/(df/dt)1=MVA1*H1/MVA2*H2

If MVA1=MVA2 then (df/dt)2=(df/dt)1*H1/H2

df2=12*30/42=8.57 Hz

Is This Answer Correct ?    1 Yes 10 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

how technical is calculated in 11kv line and lt line

2146


solar inverters was not connected to the nuteral link .this nutwral possible to any other systems

1927


What is force on parallel conductors ?

1141


can anyone explain the star-delta motor control wiring ,which wire go where and how they operate?

1500


what is the voltage rating of chiller unit sensors

2816


how does WTI work ?

2069


what are the precuation should be taken ahen installing power transformer,circuit breaker,current & potential transformer

2167


In India the supply voltage is 230 volt A.C. During the negative half cycle phase becomes neutral and neutral become phase? or what will happen during negative half cycle? how the electrons flow during positive and negative half cycle?

2086


regarding safety what would u consider the most important rules to observe when inspecting electrical equipment?

2097


WHY EARTHING NOT NEEDED IN BATTERY IN SUBSTATION

2021


what is earth pit , how we can measured it, what earth rods reference

2661


what is the Pickup/drop off ratio in BCPU relays

4704


how can we select the appropriate VCB ?

2371


-What shall be short circuit current of LV switchgear for a 1000 kva, 11.415kv, 3 phase tranformer with 5% reactance.

2186


What happen to generator if i have unbalanced load?

2159