How to calculate the value of capacitance of a capacitor
used in power factor improvement plant if we know KVAR and
voltages?
Answer Posted / raviteja vaka
for 3-ph system
Kvar=Sqrt(3)*v*i*sin(phi)
or Kvar=kw*tan(phi)
and for value of capacitance when kw or kvar is known
c=KVAR/(2*3.14*f*v^2) when capacitors are connected in Star
c=KVAR/(6*3.14*f*v^2) when capacitors are connected in Delta
I think the above information is in line with your question
If u want any further details mail me @ raviteja.vaka@gmail.com
| Is This Answer Correct ? | 5 Yes | 0 No |
Post New Answer View All Answers
How capacitor improves pf
I have a CT meter with ratio 60/5. The meter reading of previous month was 3290.49 and that of current month was 3797.26. How many chargeable units as per normal meter should be my reading.
my question is how to answer the question "you are from b.tech eee background and why do you want to go for banking
Iwould like to know barc interview questions
what is meant by surge? what we called for high currents?
What is mean by spike arrester(Voltage Operated)
what's producer of XLPE cable laying in undergroung
what is acceptance test in electrical engineering.
Why do we need interlocking in a HT metering or Ring main unit switchgear?
Why is the frequency not changed during transformation of electrical energy in a transformer?
PLEASE ANYBODY HAVE ELECTRICAL CIRCUIT DIAGRAM FOR CHMER PULSE CD 60M SPARKING MACHINE.PLEASE MAIL ME SUPRIYAAYYAPPAN@YAHOO.CO.IN.
Mention the methods for starting an induction motor?
what a function diesel generetaor turbo charger & turbo charger is more heated explain reason ?
what type of earthing do for dry fissure rock?
how is the cable tray designed & how its total length is calculated for an Industrial plant Say for Ex. (500KW Motor Load)