Answer Posted / trwer
See, Battery chargers are mainly useing for charging the
battery bank which is responsible for all control supply of
control systems such as breaker clossing coil, trip
coil,indications, protection relays, Annociators etc....
Mainly, If we are taking the supply from main, ( with
out battery back up)at the time of power failer /
breakdown how will record/ reccongnise the problem.
Secondly, Normaly we are using DC power for control.(
AC also using) for desired DC back up we can store the
supply in Battery. But inthe cause of AC how it
possible!!!!!
Moreover, in the cause control system, DC is more
efficient than AC
well, if any body can give another good answer, Most
welcome to Him. Because Knowledge is Power.....
| Is This Answer Correct ? | 1 Yes | 1 No |
Post New Answer View All Answers
How is the connection of the tap changer on the HV side been made?
What is a advantage of Self Reset Lockout ? On Fault breaker get trip & fault no longer exist then self reset lockout how inform us?
working of diesel generator ?
how you configure motorvision relay (L&T make)from DCS
what is the diff. between x'mer , isolation x'mer & ultra-isolation x'mer ?????????????
What are the advantages & disadvantages of a group electrive drive?
when will be the iocl interview results i faced interview on 8th september 2008 iam from electrical branch i faced interview for the post of electrical engineer??????????????????????//
What are dependent sources?
what is meant by tranformer impedance?
do anyone out there know where to find a compleete list on acronyms/abbreviations used in offshore electric engineering. MCB - Micro Circuit Breaker, MCCB-Mouldes Case Circuit Breaker, ELCB-Earth Lekage Circuit Breaker, ELMCB- etc.....
How to calculate the input cable rating for 10kva ups (3phase input and single phase output and also 3phase output, battery rating 65Ah)provide the formula also.thnx
can we find the inductance of a induction motor?
how to calculate the mesh earth network resistance in such substation, is there any recommended resistance values with references , thanks!
What are different types of control systems?
Q.1:What protection will be used on HT and LT side of 33/0.4 KV, MVA transformer. Indicate capacities of protective device to be used. Q.2:Which types of back-up protections are used in the power transformers? What do you understand by the term over travel in the relay? Q.3:How star and delta connected winding transformer are provided from earth fault