a power supply to be constructed from voltage cells is
required to provide Max. 20A Current with a terminal voltage
of 6v.Several voltage cells are available each of which has
terminal voltage of 1.5V & each of which can supply a max
current of 5A .the no of cells required will be ??
Answer Posted / adeel
no of cells will be 16
connect 4 cells in series to make a battery of (6V,5A)
similarly make total of 4 batteries and connect them in
parallel to get (6V,20A).
1 battery = 4 cells
4 batteries = 16 cells
Is This Answer Correct ? | 2 Yes | 0 No |
Post New Answer View All Answers
why dimmerstate always connected in star connection? what will happen if it connected in delta?
what is the difference between switchgear and circuit breakers and is there any difference between outdoor and indoor switchgear and circuit breakers , and how would you differentiate between switch yard and substation and grid station . thanks
derive DC RMS value for half wave rectifier?
When distance between two pulleys is not fixed, the tension of belt is adjusted by a) driver shaft b) driven shaft c) adjustment screw d) belt
What is an automatic controller?
im electrical engineer, could any one help me for FEWA exam questions please ?
What is the method for testing the differential protection stabilty in generator? When the time of starting What will happen if differentail protection connection wrong means?
75 kw motor take 45 amp in no load delta in star 10 amp but in load it will take 160 amp but IR velue of winding above 500 at 1kw ph to earth and ph to ph. what problem it should be?
how can calculate resistance box for 15 kw, 6 pole, RV-230, RA-42 motor
What is the diffrence (Technical & Construction ) between CBCT & Normal CT?
draw singleline diagram of star to delta and dol starters
what are factors to be consider in electrical installation like load factor,diversity factor .....
what is the voltages using in movie theaters??? why ??why not other??
what is reactive power?, why its measured in VA ? is it transient behavior of system?
Is any generator is developed which is operated with out diesal or other expensive source?