how to calculate the ac and dc wire losses with calculations
plz tell me
Answer Posted / 7anoter4
The losses of an insulated conductor in a cable –see, for
instance IEC 60287-1-1- or Neher and McGrath-are losses in
conductor, losses in insulation-dielectric losses-losses in
shield –eddy current and circulating current losses-losses
in armor, losses in metallic conduit.
Losses in conductor w=I^2*R in d.c. R=ro*length/cross
section ro is the resistivity at loaded conductor
temperature T.
ro(T)=ro(20dgr.C)*(1+a*(T-20)) a=temperature coefficient
of resistance.
Or ro(T)= ro(20dgr.C)*(T+K)/(K+20) for copper conductor
K=234.5 for instance.
In a.c. you have to add two other factors: skin effect and
proximity effect.
| Is This Answer Correct ? | 2 Yes | 0 No |
Post New Answer View All Answers
What the formula for calculating no.of earthings & size of earth strip for 100mX90m shop.
What is the resonant peak?
There is any especial requirement for motor to drive through with VFD?
i have applied for junior engineer 2 c&w for Guwahati RRB please send me last five year question paper
I'm looking for a mnaual set for a Teradyne J750. Softcopy would be preferred but I'll take what I can get.
Explain using drawings what is reverse PID action w.r.t PID controllers.
What is core CT & it's function?
IF 8255 CONTROL WORD IS 94H,Tell the chip port work mode ?
Why use the vcb at high transmission system ? Why can’t use acb?
What is an iron loss or core loss pi?
What is the power factor of a transformer at no load?
'documenˁ
What is the source of dependent source ?
fuel-air ratio in a petrol engine fitted with suction carburettor,operating with dirty air filter as compared to clean filter will be
what is the difference between megger and earth resister ??