Can anybody tell the formula to calculate temparature rise in the cable with respect to current?
Answer Posted / 7anoter4
The temperature rise in a conductor of a cable depends on
lot of factors as-for instance-:
1) The current supply way :continuous, intermittent, short-
time.
2) the cable ambient medium: air[free open, conduit, cable
tray], underground[direct, in conduit or in duct]
3) number of cable and distance between them
4) current frequency d.c.,50 or 60 Hz[ conductor resistance
depends on frequency]
5) other source of heat in vicinity-hot pipes, sunshine or
other.
| Is This Answer Correct ? | 2 Yes | 1 No |
Post New Answer View All Answers
WHAT IS THE MEANING OG (li = 7 In)
what is the best method of grounding in 30 MW generator?
What is meant by reverse polarity and how it can be fixed?
send me all basic electrical question and answers
What is Scheme Test of High Voltage Switchgear. Which tests it includes.
Salient pole alternator is more stable, why?
what does a k rating in a transformer means?
WHAT IS IM (INDEX OF MOUNTING )IN MOTORS
how to calculate the lightning arrester conductor @ no of earth pits required
What is pole of the system?
What is difference between Over Current & Earth Fault protection?
How to assume answer to electrical questions
why the projects getting loss?
Hoe do calculate the Cable size for Amps rating ?
draw the block diagram of fire alarm?