how we are measuring the winding temperature of the
transformer?
Answer Posted / pragati
hi I am Pragati
after reading those answers i found two keywords which are
RTD & thermostat.
RTD(resistance temperature detector) is used only to display
the temperature of winding. PT100 is one of RTD in which at
0degc the resistance is 100ohms. As temp. increases the
resistance increases linearly.
other is thermostat, it is an thermal switch.
DMP is one of thermostat which is having particular temp.
rating like 150deg C or 160 deg C and so on
as temp. of winding crosses the rated the switch is operated
and circuit is disconnected. This will protect our winding
from burning.
so if only display of temp. purpose we can use RTD & for
protection from burning we can use thermostat.
| Is This Answer Correct ? | 5 Yes | 0 No |
Post New Answer View All Answers
define the active power?
how to calculate the loss tangent of electrical cables
How to calculate pitch, gauge of winding wire, and No. of turns for 30HP, 3 phase, 4 poles 50Hz, 380V induction motors
What is the angle of inclination for the oil connection from transformer conservator to Bucholz relay and why?
how we find transformer capacity by ohm
Which type of transformer is used for lighting loads?
where can the transformer having vector group Yny0 be used??
How can eliminate noise problem inside temperature controller temp. variation due to contactor chattering problem.
In Plumbing services What are accessories we consider for a bathroom?
what is the responsibility of C license holder in industry?
Why you want to join non technical field when you are an engineer?
How to calculate earth wire load by formula
how we decide scurt (disc) of insulator with respect to kv rating
While HT line put on to activate ACB in low tention panel VCB tripping instantly.why it happens
Why efficiency of generator is higher than motor at a particular load?