what is onan, onaf, ofan, ofaf in transformer?

Answer Posted / mehedi islam aneek

The first letter designates the internal cooling medium in
contact with the windings.

O= mineral oil or synthetic insulation fluid with a fire
point ≤ 300°C
K = insulating fluid with a fire point > 300°C
L = insulating liquid with no me3asurable fire point.



The second letter designates the circulation mechanism for
internal cooling medium

N = Natural convection flow through cooling equipment
and in windings
F = Forced circulation through cooling equipment and
natural convention flow in the windings (also called
"directed flow")
D = Forced circulation through cooling equipment,
directed from the cooling equipment into at least the main
windings



The third letter designates external cooling medium

A = Air
W = Water



The fourth letter designates the circulation mechanism for
the external cooling medium.

N = Natural convection
F = Forced circulation (Fans (air cooling) , pumps
(water cooling))



For example: ONAN designates an oil filled unit that has
natural convection flow in the tank and utilizes natural air
convection cooling externally.



If this transformer has fans added for forced air
externally, the designation would be ONAF.



A transformer that has natural convection cooling as a base
rating and an elevated rating when fans were added later,
would be designated as ONAN/ONAF.



High fire point fluids use the designation of "K" for fluid
type. Thus a naturally cooled high fire point fluid would be
KNAN and the same unit with fans would be KNAF.

Is This Answer Correct ?    44 Yes 3 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

The transmission does not have options: a)Partition noise b) Flicker noise c) resistance d) Short noise and reason

1935


hi Is there any possibilities to find out the rotation of a shaft or something else by using electromagnectic waves or by IR rays.If s then can v change the dir., of rotation of the same by remotely?& how? plz dn't any1 say "NO r CAN'T"

1609


How the frame size of a flange mounted AC induction motor is calculated?

1520


This is reqd for a 1MW Solar power plant..We have 2DC outputs from the solar panels Connected to 2INVERTOR panels.. Output from invertor is 3ph,280v,500kva,50hz.These are connected to individual ACB.This has to be stepped up to 11KV ,1250KVA SYSTEM.Now can I use (1) one more ACBTO GIVE A COMBINED OUTPUT OF 1000KVA,280V & STEP UP THE OUTPUT BY USING a single two winding 3 ph transformer 11kv/1250kva. or (2)use the two outputs and connect to one three winding transformer of above rating..Pls suggestwith details.

2000


how do i work out the Amps of a incommer if i am running 1 37 KW motor and a 0,75 KW motor and some solinoids

1417






why output is out of phase in case of common emitter?

1664


in HT service 3ph 4 wire service Y-phase voltage shows zero . whether it is meter fault? or what be the reason ? if y-ph voltage zero ,can current is recorded? reasons for failure?

1408


what is the operating time for LBB and how does the LBB relay realise whether cb is opened or not?

1493


If I want to lift the water at a height 50m from ground level through two inch(diameter) metal pipe then what is the capacity of motor pump is required? is it possible in single phase supply or not?

1464


what is gridrotor resistance starter

1436


Can you any one explain application of buccholz relay operation and pressure relif device operation of power transformer

1439


where we use the SFU & FSU?

1980


Why do we apply both Differential and REF (HV and LV) protection schemes on YNyn configuration of a transformer?

1575


What is the procedure/activities to be taken to inject the current more than 2000A by using 2000A Loading Transformer?

1537


Why phase sequence must be same in any ht motor or generator circuit?if phase sequence doesn't same whatever will be affect on circuit?