Answer Posted / uday
MCB means miniature circuit breaker .it operates on the
basis of relay action .it is provided with a coil connected
directly to the live wire.whenever the faulty current
occures which is greather than normal current thte coil get
energised and pulls the contact.in this manner fault is
isolated.
| Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
How to select batteries required for ups and the inverter if we Known load? And how AH is selected of battery?
hi frnds what is meant by harmonics & what is meant by third hormonics,where its will occur ?thank u
1.what is difference between ATS & STS main use. 2.what is difference between ACB& VCB With symobles,and main partes, manimum range. 3.How many types of relays and main function.
how to compute kvar in substation feeder to improve power factor and sending voltage
For some transformers we are using solid neutral earthing while some others we are using resistance earthing why ?
What is the difference between UPS & inverter ? which UPS is better and whos got the edge ? what is the difference between & inverter ? which UPS is better and whos got the edge 12 V , 24 V , 36 V etc what are the advantages of 12 V, 24 V , 36 V etc and what are the disadvantages of 12 V, 24 V, 36 V etc thanks
what questions will be asked for 11/33KV licence interview APSEB hyderabad. Can any one share question and answers.
What are protections for dty type transformers
what is star delta starter? how it works? give its control and power diagram.
In the ACB breaker capacity is 2000Amp but this each phase taken 1250 But total beldibg load is 600amp or 700amp watt is the problem
What is power distribution criteria for converting single phase unbalanced residential load to 3 phase star connected balance system. Does total KW converted to 3 Phase. Means Divided by root 3.
why occ characteristics of generator is also called as magnatization characteristics ?
How to calibrate or test an LT Air Circuit breaker 440 volts, 35 KA, 800 Amps ?
What is time response of the control system?
how many types control panel of a 132/33 kv substation