in ONAN type transformer winding temperature is lower than oil
temperature at evening time but morning winding temp is higher
than oil temp what is the reason?
Answer Posted / raziq ulla
In ONAN type cooling,in the evening oil temperature is
accumulation of both atmospheric temperature of whole day
and winding temperature, so that temperature of the winding
In the evening is lower than oil temperature. At night due
to cool atmosphere continues till morning temperature of
the oil get down to its normal value and the volume of the
oil in a transformer is higher than the volume of the
winding so the heat generated by the winding is dissipated
by the system easily so that temperature of the winding is
higher than the oil temperature.
| Is This Answer Correct ? | 2 Yes | 0 No |
Post New Answer View All Answers
how external lighting design? please give examples?
what is sevice settings for mccb?How can be it setted?
how is calculated the quantity of weight in hot test xlpe?
Why we do 2 types of earthing on transformer (ie:)body earthing & neutral earthing , what is function. I am going to install a oo kva transformer & 380 kva dg set what should the earthing value?
What is the classification of hydro projects based on installed capacity?
what is induction furnance? how many phase supply given io its coil for 15 or 20 ton furnance?
how to maintain frenquncy with syncronising sub-station for distribution
What is the unit of attenuation?
how to introduce yourself
How can eliminate noise problem inside temperature controller temp. variation due to contactor chattering problem.
Explain Random and Deterministic signals?
Control wiring of a dol starter for forward and backward
66kv under ground cable how to layaing in ground any special case two ckt r runing
Testing report of Earthing of 3.15 MVa PTR.
List of equipments required foe industrial repair lab.