What is the difference between "Earthing" and "Neutral"?
Answer Posted / rahul
the earth and neutral are closly related because the
earthing is a electric wire connected to ground to make low
impedance path to avoid hazardous voltage flow through the
circuit(metal parts of electric equipments).in case of
neutral line when we check the wiring circuits and electric
posts neutral lines are also earthed .
| Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
What is the practical way to calculate the cable size for known ampere load?
what is a composite error in current transformers, why occurs & in which it will occur i.e, either metering ct/ protection ct
how can i determine the KVA/MVA rating of transformer precisely?? is there any standard test?????
Do you know what is dry-out test in x'mer
how to select diiferent power transformers of same capacity on no load loss and full load loss by economical point of view.?
Differentiate between ideal and non-ideal voltage sources?
A cable with concentric PE conductor must be used with frequency converter circuits what does its means.?
63MVA,220KV/6.9KV Transformer LV side neutral is connected to Earth pit through NGR. Whether this earth pit required to connect with near by below grouding earth mat or it is to be kept separate?
What is Annunciation?
From reading, Under voltage relay used also as phase sequence relay now, Why I use under voltage and phase sequence relay in the same circuit (ATS)?
Why magnetic flux produces an induced current?? what is the detailed procedure ?? ans plz
model question paper for supervisor trainee
Dyn1 transformer vector group testing how to do
how to calculate the torque of a motor?
what is plunger and what's the use of it in motor alignment?