1ampear me kitna watts hota hai aur elcb ka pura naam kya hai
Answer Posted / kesavan b
ELCB - Earth Leakage Circuit Breaker
It will trips if any leakage in the elctric circuit
Current will depends upon which system you are using usually single or three phase
formula
Watts = VI Cos (Phi)
Watts = 1.732 * VI ( COS (phi) )
| Is This Answer Correct ? | 489 Yes | 94 No |
Post New Answer View All Answers
witch pump used in wtp
What is difference between Harmonic and Non harmonic Capacitor Bank?
How to calculate the time setting for star connection in star delta starter? For example 10KW 3PH Induction motor.
How time response of the system is divided?
Explain mechanical rotational system?
If rotor works in clock wise what happens
What is gain margin?
What is order of the system?
What are the uses of lead compensator?
What is the effect of positive feedback on stability of the system?
If anyone would like to know or practice for FEWA papers contact me on mohamedrashad2@hotmail.com Just completed the supervisor exam in April 2021
What is a system?
we have require a Motor (1500kW, 6.6kV, 50Hz) which shall operate at 1500rpm during 30min and after it shall run on 500rpm during 15min. The same cycle shall be repetitive during the whole working days. Which method is best and economic to achieve such type of task. VFD, VVFD, Pole changing motor etc.
Difference between drift current and diffusion current?
Atwhat condition reverse power relay will act?