what is name of transformer oil ?
Answer Posted / ambuj kumar
Transformer oil is basically a fresh dielectric oil and we call it transformer oil only.The qualities that it should posses are as follows
1. High dielectric strength. around 30kv/cm.
2. High flash and pour point.
3. It should not form toxic substances at high temprature.
4. It should have good insulation and cooling properties.
| Is This Answer Correct ? | 1 Yes | 0 No |
Post New Answer View All Answers
HOW TO CALCULATE AMPs OF CURRENT TRANSFORMER IN HT Panel
help me with the question that might be ask on the interview for technical position
234 MVA Generator 3 phase Short circuit current Values required? Gen set Rating-234 MVA, Gen Voltage-18kv, PF;0.8, Xdv:23.5 %, Transformer Rating-18/380KV, 680MVA,Yndd1 two winding, Step up TR, ZT:35.50 %,X/R 4.33 Gen CB Position, CB open ,Disconnected open, Generator Running Voltage 18 Kv, Bi mistakes generator side earth switch Closed during that time short circuit current level in 3 Phase required, and how to test on site 234MVA Generator Short circuit current,
why is the conservator tank painted white on the transformer
what are the necessary basic electrical topics to learn for mechanical engineer to deal practical problems.
what is the setting of locked rotor in HT motor ? (answer expecting in percentage)
Write the force balance equation of m ideal mass element.
I have 1500/1A CT If i connect this CT in 6.6KV bus bar means what will be the voltage present in CT?
how can i change the rotation of the AC single phase induction motor and show me by diagram
What is turn ratio of a transformer?
What will happen if the voltage in my house drops from 220V to any lower voltage?
why we r not earthed Control cable of C.T. terminals
How does an induction motor start?
Why is the frequency not changed during transformation of electrical energy in a transformer?
when measure the core loss of three phase distribution transformer or three phase reactor loss, one phase shown negative watt loss. why??