How to test and satisfy the conditions of the vector group
YNd1 for power transformer?
Answer Posted / a.p.nanjappa
THIS IS ONE OF THE MANUFACTURER TEST OF VECTOR GROUP.
IN THIS TEST , THE HV RPh or Uph is connected to low voltage
rPh. /uPh. then 400v 3ph is applied. various voltage are
measured. (RS,ST,TR, R-N,S-N.T-N, r-s,s-t,t-r, r-N,s-n,t-n.
then, draw the graph,
refer to electrical hand book-transformer, any text book
also,manufacturer test report
| Is This Answer Correct ? | 3 Yes | 5 No |
Post New Answer View All Answers
wat is the first thing dat is needed, 2 lay a cable in some area??
Why mostly the HV side of transformer has Delta?
mention hazard experienced during installation
How delta connection in the primary of distribution transformer reduces harmonics?how delta connections reduces harmonics?Please answer me...Hope that question is correct.
In single phase capacitor motor, if the motor rotate reverse direction then how much power will be consumed by the motor and why?
Can you used moeller lzm1 mccb in a dc system with 125vdc and 20ka short circuit current , beside is it have 24 or 48 volt shunt ? Beside how long current can through from An MCB shunt contacts? (like Z7-AS 24 V)?
i have 3500 amp load and select current transformer and perches.how i calculate .please understand
What is 11 N1 and 12 N2 in single phase Transformer ?
why dc is used in control circuits for MV & LV switchgeras instead of ac
i am in need of AC SYNCHRONUS MOTOR 30KW. ANY ONE KNOWS THE MANUFACTURER OF SAME. ALSO MOSFET AC CONVERTER 20KVA CONT.OUTPUT.
condition Autotrip facia come on control panel of electrical transmission line?
How do we calculate transformer oil in liter from the rating of the transformer.
Draw the equivalent circuit of crystal oscillator?
what is circuit recombiner and how it is different from circuit breaker
2- What are the percentages between excitation currents in phase (R, S and T) in ∆ and Ỵ connections in excitation Current test in transformers?