Answer Posted / soumen
NGR (Neutral Grounding Resistors )is employed in AC
distribution networks to limit the fault current which
would flow from the transformer or generator neutral star
point in the event of an earth fault in the systems. It is
used when the neutral of supply transformer is accessible
and its own impedance is not enough to limit fault current.
The rating of the protection relays within the required
time.
For Grounding Neutral of Transformer or Generator,
Resistors upto 33 KV are offered for fault of short
duration like 10 sec., 30 sec., 60 sec., continuous etc.
Is This Answer Correct ? | 8 Yes | 2 No |
Post New Answer View All Answers
Why does curving the pole faces in a dc machine contributes to a smoother dc output voltage from it?
how to put cable sizing and cable glands size for respective cable & Cable Lug size in a DB sectors???
WHAT IS THE MEANING OG (li = 7 In)
Sir, plz tell me how droop setting is done in parellel operation od DG set ? please give practical example ?
What is the drawback of class b amplifier? How is this minimized?
in wind mill use 2100 kw asychronous generator ( induction generator ) rotor voltage : 3300,stator voltage : 690, rpm : 1511 type : MRL063E04 ' we check rotor resistance magger value found following. R-EARTH - 00 M.OHM,Y-EARTH-34 M.OHM,B-EARTH- 33M.OHM R-Y: 31 M.OHM, Y-B: 00 M.OHM,B-R :33 M.OHM HOW CAN I TAKE DECISION?pls ans. quickly
1.why should we connect the measuring instruments in l.v side in short circuit test of a transformer? 2.why the power factor is less in open circuit test of a transformer?
how can calculation ate Amps for cabel. Ex-for 1sqmm wire hou many amps we can draw
In DC generator, we use commutator, having no. of segments. Then how it is possible to get a half wave of voltage and current for half rotation of armature?
ACB & VCB how do work and saftes and how can maintenance in this and parts name show with picture
What is the effect of pi controller on the system performance?
What will happen if the d.c. Machine is operated below rated speed?
How can I calculate the Mega watts required to run a plant having many electric motors and other electrical components.
what is the value of combined earthing in general electrical circiut?
Tell me in detail about c.t. And p.t. ?