How to calculate the diesel generator efficiency? what
details are required to identify the running diesel
generator sets with 1000 kVA & 180 kVA?
Answer Posted / sanat khan
Answer
# 4 Units generate/litres consumed
Thanks for Marking this Answer
Answer
# 1 The diesel generating set efficiency is calculated
interms
of units generated per liter of diesel consumed.
To monitor either you need to have a diesel flow meter
fitted in the supply as well as the return line after the
governer and the KWHr ( Units )generated.
For less accurate measurement a dip readings can be take
along with the units generated predetermined time.
Thanks for Marking this Answer 0 M.s.srinivasan
| Is This Answer Correct ? | 8 Yes | 9 No |
Post New Answer View All Answers
i want to model paper for section engg.
what is class of SPD and dittels of all class ?
We have 250 KW x 2 motors, which are load from 25% to 100% varying load in every minute , so how can we compansate the power factor. pl give your opinions on the above subject.
Please elaborate th´evenin’s theorem?
Difference between HRG and NGR. Are they both the same thing
why did youi choose this career?
Whether IP65 enclosure box blocks ventilation if driver for LED have to enclosed inside IP65 box
What is knee point voltage?
Single line diagrams for star to delta and DOL starters.
Do Phase angle measurement have any application in freq/harmonics measurement? If so how?
what is the purpose of silicon dropper used in battery charger?
The screw thread commonly used for transmission of motion is one of the following types of threads
What is icu and ics in Acb and how many time icu or ics passes from breaker?
How to select, design,size & calculate for 11 KV/33KV/66KV/132KV/220 KV/440 KV circuit breaker for HT side of transformer protection/HT distribution protection?
What do you mean by the zone of protection?