how to calculate capacitor rating for an induction transformer
ex.for 12 mva furnace calculate capacitor rating
Answer Posted / wareagle
#1 you almost got it right. It should be 144 - 92 = 52
sqrt(52)= 7 KVAR. You should know better.
Is This Answer Correct ? | 3 Yes | 0 No |
Post New Answer View All Answers
how to protect motor in dol starter having capacity of 30 hp.40 hp?
What is use of starter and choke in tube light
how can we determine size of a cable by knowing the kw or current rating of a load?how can we calculate the resistance box of a slip ring motor?
Is it posible to instal one more SMDB from the existing SMDB and is it practical.
why transformer ratings in kva? & DG ratings in kva? & Motor ratings in kw/HP?
where lt & ht capacitor used
What do you mean by transformation ratio of instrument transformer?
Why Ac Systems Are Preferred Over Dc Systems?
What is difference between Harmonic and Non harmonic Capacitor Bank?
Installation method of self treated earth electrode.
How to calulate Locked rotor amper(LRA) for compressor type motors?
in general it is observed in power stations, the tertiary winding is used in higher rating Y-Y auto transformer but not in Y-Y power transformer. is the tertiary winding is compulsory then why it is not using in power transformerÂ
State superposition theorem?
What is the current carrying capacity of 0SWG,3SWG,10 & 12 SWG solid bare overhead copper conductors?
LT cable fault chaecking equipment and to find out the distance at what distence it failure . Name and where it is available?