how to choose the cable size for 100A(is there any formula
please update)
Answer Posted / shirish
Theory for Cable Sizing.
From Ohms law, the voltage drop in an electrical conductor is
V = I R
where
I = Current, amps
R = Resistance, Ohms
The electrical resistance can be derived from the properties of the conductor material.
R = ρ L / A
where
ρ = Resistivity, Ω mm2 /m
L = Length, m
A = Cross sectional area, mm2
Watch the units in the above equation.
The resistance can also be expressed in terms of the material conductivity (ψ) which is just the reciprocal of the resistivity.
R = L / (ψ A)
Table 1. Typical material electrical conductivity
Material Conductivity, ψ
Copper 58
Aluminium 36
Mild Steel 7.7
Combining Ohms law with the resistance expression, we get.
V = (I L) / (ψ A)
Now, we can define an acceptable voltage drop in a conductor. I have calculated the voltage drop that was used in several published tables and get around 5.5 Volts.
We could therefore re-arrange this equation to give the cable size. But cables come in standard sizes measured in mm2. In addition, you also need to consider the maximum current for each cable size.
Table 2. Conductor sizes and maximum currents
Cable Size, mm2 1.5 2.5 4 6 10 16 25 35 50 70 95 120 150 185 240 300
Maximum current, A 13 21 28 36 46 61 81 99 125 160 195 220 250 285 340 395
So, the theory is relatively simple, let us now see how to use the program.
| Is This Answer Correct ? | 0 Yes | 2 No |
Post New Answer View All Answers
For refrigerators the motor current is raised beyond its rating on both conditions when the voltage of the system is more(say 270v) than the rated voltage(220v) as well as when the voltage of system is less(say 160v) than normal voltageof 220v, why explain?
Define characteristics impedance?
What’s electric traction?
write a program that prints prime numbers from 1-20 in digonal form
DG SET BLOCK DIGRAM
how we can calcultae the short circuit level for bus bar
what will happen reduce the transformer voltage from 415v to 406v, is it save the energy,? are this methodis good to reduce the energy.?
What will be the effect if I use inverter as UPS mood?
PLZ EXPLAIN CORONA,SKIN,BIRD PALE,SPAN,SAG Effects of power cable.
why and how voltage sharing in transformer, during magnetic balance test ?
How does zener phenomenon differ from avalanche breakdown?
what is class of SPD and dittels of all class ?
Why does the Solid state Rectifiers for 3-ph brake motors sometimes have 2 & sometimes 3 output terminals?
Is neutral transformer can be called as control transformer?
define the active power?