how can synchronous generator can be used as synchronous
condenser?
Answer Posted / shekhar nainwal
PREVIOUS ANSWER IS TOO PRACTICAL
ANS-for operating generator as a synchronous condensor it should be first declutched from turbine so now it takes power from the busbar and operates as a motor operating on no load
| Is This Answer Correct ? | 1 Yes | 0 No |
Post New Answer View All Answers
what is the criterion for selecting vector group of Transformers ? i mean how to decide vector group of Generator transformer, substation trasformer and transformer at consumer end
could you measure current in parallel?
(1)Can earth and be conected together (2) what is the diferent between earth & neutral
What is the accepted limit to increase the choosen transformer capacity over the load and why ?
what is formula for calculate thermal overload in new numiricalrelay( not in bimetal relay)?
can we install HT panel & LT panel side by side or how much clearance is required ?
mccb service sittings be done?
In ht capacitor ckt we are using LBS Panel it having isolator with fuse, one of HT fuse flash over, so what is reason behind this event.
What do you mean by ratio correction factor of instrument transformer?
how to protect motor in dol starter having capacity of 30 hp.40 hp?
Why we are going for converter transformers for DC drives application instead of distribution transformer?
what is alluminium arm in ab conductors
what is the best transformer oil breakdown voltage?
Safety of on line ups
2 v/500amp/hr to 1.80vpc at 20 degree celsious 2v/5ooamp/hr to 1.75 vpc at 77degree farren .this is the capacity of a battery .what is the meaning of this . can i get a detailed explenation