how to measure flow with dp

Answer Posted / omak

By using orifice plate we can measure the differential pressure between the upstream and downstream. This diffferential pressure is proportional to the sqaure of the flow.ie Q2 = DP
(or) Q= sq. root of DP. So by using square root extractor we can get the volumetric flow.

Is This Answer Correct ?    12 Yes 1 No