What is the difference between MCB & MCCB,
Where it can be used,
Answer Posted / b.manikandan
MCB
* MCB means miniature circuit breaker.
* MCB trip current may be not adjustable in the small
ratings.
* MCB can used low current is not more then 100amps.
* MCB is used for single phase suply only.If we want mcb
for three phase suply we can use 3 mcb.
MCCB
* MCCB means moulded case circuit breaker.
* MCCB trip current may be adjustable in larger ratting.
* MCCB can used higher current areas more then 100amps.
* MCCB is used three phase suply only.
B.MANIKANDAN
| Is This Answer Correct ? | 7 Yes | 0 No |
Post New Answer View All Answers
What are the advantages of the three-phase motor over single phase motor?
What is mean by STUB protection?
how to design step down 12 V, 1mA small transformer from 220 V AC? Because according to VI relation and power transfer it results bulky...
how to calculate the breaking capacity of different breakers.
Disadventage of cable-gland earthing if any ?
What is the formula to calculate the size of Aluminium and copper cable?
Why squirrel cage motor can only use with low starting loads ?
which fault is severe and why?between lll fault and lllg fault which fault is severe and y?
what is doubling factor in making current of a breaker?
1.what is difference in maintain Hz again Hz in USA ? 2.how to calculate the battery AH? 3.why are yearly maintained in transformer how many tests in required?
SUTIABLE FOR ohm's law super conductor
what is PWM in IGBT and how it works for drive.?
During FEED, you will have all the information with regards to cable. How will you calculate the MTO for MV and LV Cables? what are your considerations?
How time response of the system is divided?
What is dc current source?