What is the technical formula to calculate the load taken by a motor in Amperes ?
Answer Posted / anand_gupta112001
Amperes when horsepower is known
1) HP x 746/E x Eff x pf (for single phase)
2) HP x 746/1.73 x E x Eff x pf (for 3 phase)
Amperes when kilowatts are known
3) Kw x 1000/E x pf (for single phase)
4) Kw x 1000/1.73 x E x pf (for 3 phase)
Note: I = Amperes; E = Volts; Eff = Efficiency; pf = Power Factor; Kva = Kilovolt-amperes; Kw = Kilowatts
| Is This Answer Correct ? | 3 Yes | 3 No |
Post New Answer View All Answers
why impudance relay used for medium transmission power system? why not others?
I am having a 1500 KVA transformer whose secondary current is 2086A and my connected load is 1000 KVA, I am having 400 KVAR APFCR for PF improvement what ratio of CT should i install in LT EB Bus to get optimum PF improvement?
how are reversing the direction of rotation of dc motor
where can i get vijaya electricals limited in hyderabad interview auestions can u give me the website address plz
is it possible to have dc motors on single chip
EHV current carrying parts need to have smooth finish,then how can a 245kv GIS with emery finish can run so long?
What is the difference between earthing,ground&nutral?
WHAT IS MEANT BY TV TERMINAL IN 500MVA TRANSFORMER?
send me any model test paper of clerical post of state bank of india.......
What is the Basic Difference bitween Long Shunt Connection and Short Shunt Connection in DC Generator?
If two Transformers are connected in parallel having impedance of 50KA in both transformers will the impedance increase or decrease after connecting transformers in parallel?
How to calculate Air conditioning capacity for a telecom BTS shelter?
how many types of motor can be used in washing machine
how to setting voltage RTCC panel
what ispositive, negative, zero sequence impedence?