state the functions of different parts of star delta starter.
Answer Posted / rajkumar85
the diffrent parts in star delta starter are star contactor,
delta contactor, main contactor and mainly timer.when you
press the START button first the star contactor will engage,
and closes its contacts.at the same time main contactor also
engages through n.o of star contactor.the timer is cut the
star contact supply after a preset time delay then engages
the delta contact in to supply lines.now motor will run in
delta, (full speed).
| Is This Answer Correct ? | 13 Yes | 1 No |
Post New Answer View All Answers
What is power in wattage of 8.5 TR AC
what is kondo syatem in eletrical traction
i am an maintenance engineer. one distribution board have 5 feeder. recently its ELR trips frequently, but it take some times after trip( 10min,20min..)but 3 feeder no load. two feeder only loaded. i checked one feeder IR value all values are above 50Mohm.but B phase to Earth is only 9Mohm.any problem about low value
Why the cores of large transformers build up of circular cross section?
how to calculate transformer load?
how to calculate units consumption for a 12 hp motor /hr.
Determine the BTU size of an aircon for 20 sq metre room
1)we have 1000 cfm Blower,Dia-1Mtr,Velocity of air 94 m/s 2)We have Natural Air velocity 94m/s 3If i Put Wind Mill in natural air ,speed is 94m/s Then it will generate Assume 100kw 4)If i put same wind mill across the Blower,air speed is same 94m/s now the Question is Will it generate 100 kw?
List the power rating of any 5 important electrical appliances used in houses.
How to select transmission line type (i.e. 11kv or 33kv) for new established industries
PLZ EXPLIN ABOUT CLASS PS CLASS CT .WHY THEY R DESINED AND FOR WHAT PURPOSE?WHY OTHER CT CANT BE USED AS PS CLASS CT? EXPLAIN IN SIMPLE LAUNGAGE IF POSSIBLE PLZ GIVE CIRCIT DIAGRAM?EMAIL-RAJ_SINGH_0376@SIFY.COM
Could you measure voltage in series?
hi guys please tell me the procedure for mesuring the coil resistance of 3ph induction motor?
From what on-site components does the HT panel monitoring the bus-bars in a 11kV system take inputs?
Draw the DOL starter and star delta starter drawing?