What happen when ct secondary are open circuited? why same
thing is not happen in ordinary transformer?
Answer Posted / bhatt
If secondary of CT is opened and as we know that primary
always flow the current and by transformaton action
secondary must flow the current but in our case secondary
is opened hence Extra high voltage is induced in terminals
of secondary which can be fatal.
In case of ordinary transformer if secondary is open
primary flows only no load current hence secondary voltage
is only rated secondary votage which is not as danger as in
the case of CT.
| Is This Answer Correct ? | 1 Yes | 0 No |
Post New Answer View All Answers
what are the specifications we must look at to select a relay for any capacity motor?
There is any especial requirement for motor to drive through with VFD?
What happen Grid EARTH plat got cut.
for 100 HP Induction motor service factor is 1.2(SF) we placed a VFD at the motor side load is balance with 0.3 Amp's Phase to Phase but at incoming of VFD load is un-balance with 10 to 20 Amp's what will be cause of load un balance
54 Comments Alok and Bhanu play the following min-max game. Given the expression N = 38 + X*(Y – Z) where X, Y and Z are variables representing single digits (0 to 9), Alok would like to maximize N while Bhanu would like to minimize it. Towards this end, Alok chooses a single digit number and Bhanu substitutes this for a variable of her choice (X, Y or Z). Alok then chooses the next value and Bhanu, the variable to substitute the value. Finally Alok proposes the value for the remaining variable. Assuming both play to their optimal strategies, the value of N at the end of the game would be?
what are the application of over current relay?
How many types of circuit loads are there in a common electrical circuit?
What is a advantage of Self Reset Lockout ? On Fault breaker get trip & fault no longer exist then self reset lockout how inform us?
What is the criteria that generally follow by distribution licenses to fix contact demand of their industrial customers?
What are m circles?
What happens if the series current double?
What are your personal skills and abilities for such a Master Course and your possible preparation to undertake this course?
difference bewteen reverse current and alternating current
When calculating the speed of a rotor required for a particular frequency of synchronous generator we use the equation 60f/p Is this p is the number of pole pairs of rotor & do we consider the number of pole pairs in the stator is 1?
what is th basic difference between a d latch time line and a d flip flop time line???