single phase can run in PVC conduit. Three phase can also
run in one PVC conduit. But two phase cannot run in one PVC
conduit. WHY? reply plz....awaiting your answer.
Answer Posted / bhatt
In PVC conduit, one can run single phase, two phase and
three phase but two phases is not allowed in metalic
conduits as two phases can not cancel out magnetic field
and metalic conduit can induce voltage which can lead to
fatal accident.
| Is This Answer Correct ? | 11 Yes | 2 No |
Post New Answer View All Answers
Differentiate between voltage and current feedback in amplifiers?
While converting delta into star or star into delta ,the three values of resistances remains unchanged .Find out the value?Let In star R1=x;r2=x;R3=x On converting into delta,R12=x;R23=x;R31=x Find the value of x
what is the power rating of CPU, CRT type moniter, LCD type moniter,scanner Approx.
we have amp, voltage, kw, length detail then how to calculte copper & alluminium size of conductor of 3-phase induction motor
how i can calculate the size for fire cable
what is meaning of sympathetic tripping with respect to relays and give the values for current carrying capacities for copper and aluminium cables from 16sq mm to 500sq mm
give me atleast four differences between circuit and network
what is load vs Torque curve & why it is used?
What are the types of power in electrical power?
What is the abbreviation of NGT panel
how can we say that stator magnetic field rotates with synchronous speed?can we derive?
define reflection method?
I HAVE BEEN SELECTED FOR APGENCO A.E(ELECTRICAL) 2008.HOW MUCH WEIGHTAGE FOR INTERVIEW AND WRITTEN TEST.HOW I HAVE TO PREPARE. PLEASE GIVE INFORMATION IF U KNOW.WHAT ABT G.D THIS TIME.CALL RATIO 1:2
why on axial hitting up of air blast on hydrogen produced in oil circuit breaker,temperature rises of the core of the arc?
state the working principle of incondenscent tube?