Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

what are all the daily preventive maintainance carried out
in transformer?

Answer Posted / chandrasekarapandian

1.Transformer Oil level
2.Winding temperature,Oil Temperature
3.Transformer noise.
4.Silicon gel condition(should be in dark blue colour)
(if it changed to brown we should replace)

Is This Answer Correct ?    3 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

While converting delta into star or star into delta ,the three values of resistances remains unchanged .Find out the value?Let In star R1=x;r2=x;R3=x On converting into delta,R12=x;R23=x;R31=x Find the value of x

1873


What is the difference between shortcircuit current, rated current of cable & MCB with example? What will be the size of cable required for 5.5 KW motor (Full load current 10 Amps approx.), Starting current with DOL is 120 Amps. Aprrox. Short circuit current with LLLG fault is 2000 Amps Approx.

2002


for a 400kv t/m line with 10 ampere current will corona occur?

2145


what is the current density of copper & alluminium.

1994


why the neutral line is not giving shock to us if we touch it ?

1712


How delta connection in the primary of distribution transformer reduces harmonics?how delta connections reduces harmonics?Please answer me...Hope that question is correct.

2149


how maney type tempereture measurement ?

2201


what are the different sizes of U.G. cable & where these cabl;es are used according to voltage ..

2058


HOW TO SET THE EARTH FAULT SETTINGS IN ACB????????????

2119


description about dry type transformers

1837


10 tube light connect in mcb breaker.one tube light is fault.so breaker is tribe.how fault is rectified.(using 3wire phase,earth,neutral)

2587


what is transient voltage?

2199


The transmission does not have options: a)Partition noise b) Flicker noise c) resistance d) Short noise and reason

2383


When is lag lead compensator is required?

1071


CBCT selection

2231