What happens if ac is applied to dc systems and vice versa?
Answer Posted / deepak mishra
if dc supply is given to ac system than equipment like
transformer and motor(which works on induction principle)
burns. it is due to so much heat generated in windings as
flux does not vary in dc supply. while giving ac to dc
system there will be a increse in losses and material.
| Is This Answer Correct ? | 6 Yes | 0 No |
Post New Answer View All Answers
If the line voltage is reduced to 75% of its rated value then by what percentage current will reduce ?? 75% 25% 50% no change and why ?
HOW DO YOU CAN CHECK A 15KV DIODE, WHETHER IT IS OK OR NOT?
When will you multiply and devide with derating factors to the actual value while sizing the cable?
how to compare with Relay settings for HT< panels, RMU panel, and PSS CSS transformer?? 1) Load amps, 2)Tripping time, 3) CT ratio, 4)Cable size 5) Transformer KVA rating 6) transformer full load amps
can u give me a brief idea about power line carrier communication ??
How many methods use the load flow solution?
why the carbon brushes are broken in srim while the motor runningtime
what are the Alarm, Trip & Safety equipment (Issues) present in Power Transformers pls Mail it to ashokbabunhce@gmail.com
can i connect the two phases of scott connected transformer,if not why?
When a single pase capacitor run motor- run on 230vac and Case(1)run with 8 Mfd 250 vac.capacitor , Case( 2) run with 8 Mfd 400vac capacitor. What is difference between both case regarding power ,efficiency etc?
what is the isolation transformer. what is the isolator?
what is the necessity of under ground cables ??
Draw the vector diagram and condition for the following: 1) Dyn1 2) Ynd0 3) YnYn0
How to calculate the External Resistance required for 60HP slipring motor in case no any data of the Motor is available???
How to measure size of cable on a given load