draw a circuit diagram connecting transformer OLTC- RTCC-
VCB-Marshalling Box otherwise Explain in words
Answer Posted / alleysyed
OLTC stands for On Load Tap Changer, which means that a user
can change the taps of transformer winding without
disconnecting the transfomrer from the supply. Taps are
changed in order to regulate the voltage. OLTC has number of
taps . They may be 10, 11, 16 , 20 or the customer specified
rating.
Marshalling box is a box in which manufacturer of
transformer bring alarm and trip contacts signalling from
the accessories associated with the transformer. For
example, Oil temperature indicator installed on the T/F
provide a signal of alarm when the temperature of oil
exceeds the specified limit of Indicator. If temperature
exceeds more, it send the trip signal to Marshalling box,
which disconnects the transformer from main supply and
vacuum Circuit Breaker is tripped. VCB is installed on the
High Voltage side of the TF in the HV Protection panel.
| Is This Answer Correct ? | 31 Yes | 5 No |
Post New Answer View All Answers
Can you any one explain application of buccholz relay operation and pressure relif device operation of power transformer
what is meant by class 1 E in electrical power supply?
what is the grounding Calculation formula? spouse i want to provide grounding to 3phase 18kw motor or i want to provide ground to 3phase 10kva dry type transformere or you give me any exemple...... Thanks.
In motors how many types of cooling systems were used?
How to convert 2 phase to 3 phase electricpower in induction moter?
what is mean by ideal infinite bus? why it is required to consider in fault short circuit calculations?
I am experienced with house and industrial wiring but I don't have any licence how can I apply an licence and which type of licence i can get i didn't complete deee just only experience
Can anyone please provide me details of MCCB/Contactor/SFU rating calculations for a motor feeder..for example 50 kw.. not from type-2 cordination chart. i want manual calculations..
how to compare with Relay settings for HT< panels, RMU panel, and PSS CSS transformer?? 1) Load amps, 2)Tripping time, 3) CT ratio, 4)Cable size 5) Transformer KVA rating 6) transformer full load amps
What is the importance of earthing?
why Induction Generators are not "Black start" ? and apart from WTGs where this types of generator are generally used?
is the value of inductance depends upon the evalue of thitha in doubly excited machine?
wat system call?
what is the stear deltaprinceple?
Give atleast 20 alternating current apparatus and devices.