If u have 60KVA UPS, than tell me how systems ( computers )
u may connect?
Answer Posted / bala
Consider
200 VA / System
60kva x 0.8 = 48 kva ( Efficiency =0.8 )
Calculation
= 48000/200 =240 workstation or system
Is This Answer Correct ? | 12 Yes | 0 No |
Post New Answer View All Answers
how calculate gd2 of ht motors
what is difference between window type and wound type transformers?where we will use window type and wound type transformers?
Q.1:What protection will be used on HT and LT side of 33/0.4 KV, MVA transformer. Indicate capacities of protective device to be used. Q.2:Which types of back-up protections are used in the power transformers? What do you understand by the term over travel in the relay? Q.3:How star and delta connected winding transformer are provided from earth fault
WHAT ARE THE DISADTAGES OF SINGLE-WIRE-EARTH-RETURN SYSTEM USED FOR RURAL ELECTRIFICATION?
Dry type transformers
How can we calculate the motor frame sizes?
DEFINE BREAKING CAPACITY OF BUSBAR & HOW IT IS CALCULATED?
what purpose to use excaiter in DG.?
What is difference between Sample test and Routine test in safety standard?
sir vizag steel ka junior trainee ka paper kitne number ka ayega
why high speed tripping relay is used in protection circuit why not normal relay
What is s-domain and its significance?
why u r living from presentaly working.
How to test REF relay testing for LV panel as per Kahramaa standard?
Explain the operation of grid connected central solar inverter ?