What difference between MCB,MCCB,RCCB,ELCB please explain briefly with its rating.
Answer Posted / karthik.j
MCB means Miniature Circuit Breaker -- it is used for upto
100Amps in the motor feeders.
MCCB menas Moulded case Circuit Breaker -- it is used for
25oAmps to 800Amps in the motor feeders.
ELCB means Earth Leakage Circuit Breaker -- it is used to
trip the Circuit breaker if any leakage fault occured means.
RCCB means Residual Current Circuit Breaker -- A residual
current device (RCD), or residual current
circuit breaker (RCCB), is an electrical wiring device that
disconnects a circuit whenever it detects that the electric
current is not balanced between the phase ("hot") conductor
and the neutral conductor. Such an imbalance is sometimes
caused by current leakage through the body of a person who
is grounded and accidentally touching the energized part of
the circuit.
| Is This Answer Correct ? | 8 Yes | 3 No |
Post New Answer View All Answers
what is reactive power?, why its measured in VA ? is it transient behavior of system?
i need mat lab program to find out the transmission line losses,regulation and losses
what is the benefit of floating our DC source? if i have two floating DC source of which 1 has a ref voltage of -21VDC and the other of -18VDC. can it be connected in parallel to share a common ref voltage? if not, how do i make both sources to be of common ref voltage? tks
i am in need of AC SYNCHRONUS MOTOR 30KW. ANY ONE KNOWS THE MANUFACTURER OF SAME. ALSO MOSFET AC CONVERTER 20KVA CONT.OUTPUT.
Dear all i want to know SEWA Electrical Supervisor Licence test Previous Year Questions ? If any body know please send to me zohairaukllah@yahoo.com
lorteny method
WHY THE DIMENSION OF TWO SAME RATED MACHINE IS DIFFERENT ?
What is the selection process of breakers. Can any one please give a formulation on same?
3 phase Motor will be given 2 phase after 2 to 5 second we given 3rd phase so Motor Run sum-time in forward or sum time run reverse direction. All time phase sequence is not change. Why motor run in reverse direction? Please Explain........
What is open delta Xformer? It's adavntages & Use?
i have 90kw motor.so i choose connect cable .please what is parameter checked so please give to formula
Explain the working principle of Synchronous Generator and Assynchronous generator?
What is the principal of motor?
What tests should i carry over on a newly rewinded DC Generator with voltage rating of 38 volts and current rating of 350 amps, to certify that the machine is OK?
Star Delta Diagram with full description