what is the difference between the 94 lockout relay and 86
lock out relay. I have noticed that the 94 lockout relay is
activated when the distance realy is activated and 86 is
activated when the 87T differential is activated. but why
can't the same lockouts be used for both the protection
schemes

Answer Posted / ajay khandait.

Lockout relay is handreset relay in this case both the
relays are hand reset relay. only difference is that 94
lockout relay is used for line protection and can also be
provided with auto reclosing facility.
If the auto reclosing is not successful then in that case
94 goes to Lockout state and shall be manually resetted.


In case of 86 there is no Auto reclosing feature available.
It goes to lockout state directly.

Is This Answer Correct ?    2 Yes 5 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

What are the uses of stepper motor?

709


control & auxilary circuits used for circuir breakers

1469


please suggest some good universities with low cost iam in totally full confusion so please help me my profile gre 283 and ielts 5.5

1170


In Dyn11 power transformer if any one of the 3 phases connected to earth in star connected side then please explain effect of the current flow in delta connected side of transformer.(In this case if one phase is shorted to ground in star connected side then we observe the current flow in two phases only not three phases in delta connected primary side. Please explain why it is so?)

1296


What is Electrical Grade Aluminum for Tubular BusBars. i am confused between 6063 and T6 or T5 and what is BS 2898 and BS 159?

1412






what is the reqirred voltage in HT motor to get full RPM on no load test?

1552


What is error of a measurement?

614


how to set relay setting? and example calculation...

1512


Can anyone please provide me details of MCCB/Contactor/SFU rating calculations for a motor feeder..for example 50 kw.. not from type-2 cordination chart. i want manual calculations..

2091


what is the carona effects meaning in HT line transmmission system

1516


how can i find ct ratio of meter by seeing name plate of meter and how it should be used in MF calculation if it shows only-/1???

1247


What are hrc fuses and where it is used?

720


What is process of anneling transformer core

1457


WHY THREE PHESE SYSTEM VOLTAGE APPLIED IN 440 VOLT

1913


Why an ac systems are preferred over dc systems?

627