What happens if a three phase induction motor is suddenly
single-phased while running? Which type of winding
connection will be affected?
Answer Posted / rajesh sharma
1.if motor conected in STAR than motor two winding burn
2. if motor in DELTA motor one winding burn
3. time duration is depend on load for burning
4. in star R phase is blown than y/b winding burn because
that winding get 440volt and take to much current
5. delta if r phase blown than y pahse winding burn because
only that winding get 440 supply other no.
| Is This Answer Correct ? | 3 Yes | 0 No |
Post New Answer View All Answers
In how we connect watt meter for open & short circuit test of a single phase transformer.
in an electronic tri vector meter when the current and voltage sequence changes ? what is the effect of phase sequence on recording of meter
A 50Hz,4-pole,3-phase,star-connected synchronous motor has a synchronous reactance of 12ohmsper phase and negligible armature resistances.the excitation is such as to give an open-circuit voltage of 13.2kilovolt.the motor is connected to 115kilovolt, 50hertz supplying. what maximum load can be the motor torque,line current and power factor?
what are the installation procedure of high voltage power transformer,CT,CB&PT?
What is the Minimum winding resistance of motors ( small & big)? referance range
How to configure the drives in PLC, through Profibus commnication. And to how to address it?
what is the need of starter in tube light and what type of starter is used in that?
What are the two basic types of transformers?
what is p.s impedance measurement test in earthing transformer?
if any house we instaled a 1.5 ton ac and its phase cable of wiring is installed but netrual cable of wiring not instaed. my question is that is neutual of house(for other wiring is capable for ac load or a sepeart neutrual wiring required
How relay works, reverse relay, master relay, os relay, earth fault relay and what is its setting point
Why insulation level follows this order? transformer < bus bar < circuit breaker & Isolator < transmission line.
xpression 'document.FrmQF.myemail' [
what is smartµ grid technology?under coal gassification?
how to find out 3 phase complex power in per unit in unbalanced system?