how much current a 100 sq mm busbar will carry?
Answer Posted / mojinkoshy
It depends up on the material of the Busbar.
ie. if you use cu bus bar (SWITCH BOARD current RATING / 1.2)= CU. busbar area. if you use Al. bus bar (Switch board current rating/ 0.8) = Al. busbar area.
the bus bar area is normally expressed as 50X6 or 2Nos. 100X12 not like 100sq.mm.
| Is This Answer Correct ? | 4 Yes | 2 No |
Post New Answer View All Answers
which connection is safer series or parallel?usually which connection we prefer at home?
can i connect the two phases of scott connected transformer,if not why?
Why space heater is required for each verical bus bar chamber? if one space heater is adequate or not for anti condensation?
What does the term supermesh means?
What is different type of Electrical curve and how it protects the equipment's while up-normal situation?
briefly explain the main blocks found in a microprocessor based system
Differentiate between kirchhoff’s first law and kirchhoff’s second law?
Why the magneti fields are not passes from southpole to north pole
What is zero of the system?
What Should be the value of Vector Surge angle at Tripping and how to calculate it?
how we decide scurt (disc) of insulator with respect to kv rating
What is the difference between isolators and electrical circuit breakers?
How to calculate the size of earth cable to earth the neutral of UPS ?
How to know about the rating(voltage and other) of induction motor if its name plate is missing at the manufacturing site.
WHAT IS counter flux IN CT?