Answer Posted / s@nz
LBB as ssaid above it means LOCAL BREAKER BACK UP RELAY is a
back up protection for local breaker (CIRCUIT BREAKER) a
predefined time set in the relay and when the circut breaker
for LBB is kept does not operate ( during fault conditions)
in the pre defined time the surrounding breakers are given
trip command by the LBB relay to restriced the fault..
| Is This Answer Correct ? | 78 Yes | 13 No |
Post New Answer View All Answers
If I want to replace a 26KW Slip ring Motor with a Squirrel Cage motor & Drive (for a Hoist Application). How can I approximate the Motor & Drive HP required in new Setup.
why we are using earth pit in sub stations.?
please send the IS strandard for electrical to sakthi_murugan86@yahoo.co.in
How much load can be taken for chiller from 1500 kva transformer
what happen if drive input fail momentry at 48.5 HZ frequency?
How would you calculate power loss in a resistor?
What is a slack bus?
what are the accessories need to be added while doing estimation for the following: 1.MCCB 2.MCB 3.ACB
what is magnetizing and demagnetizing current in generator and motor?
-What shall be short circuit current of LV switchgear for a 1000 kva, 11.415kv, 3 phase tranformer with 5% reactance.
What do you mean by a phase angel of instrument transformer?
what is the best method of grounding in 30 MW generator?
what are the standard IR values should be of R-E, Y-E, B-E, R-Y, Y-B, B-R of VCB in closed condition and in open condition for 500KVA & 1000KVA transformers. and what is the acceptable range when tested by 5000V megger.
Why does amplifier gain reduce?
Suppose a 3 phase, 2 pole, 440V induction motor is driving a flywheel of 600mm diameter, 150kg mass. By using v-belt and pulley, the speed is increased to 4500 RPM. What will be the effect on motor current?