Why TAP changer provided in primary side of HT
transformer ? and why not in secondary?
Answer Posted / k1
There are two reasons; one reason from electrical and the
second one from practical point of view:
1- Low current on HV side makes tap changing smoother and
lowers stresses on the diverter switch.
2- HV windings are generally on the LV windings(consider
concentric HV and LV windings). Therefore the wiring of the
taps would be easier in comparison to the case where the
taps on LV side may be wired through HV windings.
| Is This Answer Correct ? | 7 Yes | 6 No |
Post New Answer View All Answers
Why Transformer Neutral having one earth pit ( more earth electrode resistance) whereas body have many earth pit ( less earth electrode resistance)?
Why we are use dol starter up to 10 hp
Explain Continuous and Discrete signals?
Explain the different methods used in the choice of rotor slots for reduction of harmonic torques in an induction motor.
plz send me HPCL apptitude paper.. maulik_elect@yahoo.co.in
Why do not we prefer non conventional sources of energy to conventional sources?
What is real time power factor control panel(RTPFC)?
How to decide whether A / B / C / D curve type MCB should be used?
why impedance relay is used for medium transmission line protection
sir i want previous entrance exam papers for written test
why chock were used in old tubelights but are not newest tubelights?
According to underground cables a) stress b/w sheath & conductor is high b) inrush of core & conductor
What is difference between slip rings and carbon burushes?
What is difference between Over Current & Earth Fault protection?