Answer Posted / murugesan
First ensure both I/P and positioner air supply are as
it should be before starting up control valve
calibration/stroke checking activity. Then take any of loop
or multifunction calibrator based on the instrument
availability in your plant for Ex 707Ex, UPS-III-IS, UPS-
II, UPS-IS, DPI610 IS (connect series with 24 VDC supply),
UNOMAT and 725Ex
And select “mA source with 24V DC” option and connect 4-
20mA source to I/P converter and simulate appropriate mA to
check the stroke. Normally control valve stoke checking is
called as control valve calibration.
| Is This Answer Correct ? | 2 Yes | 0 No |
Post New Answer View All Answers
how we are selecting instuments by differentiating certain instruments in 4 to 20 ma range and certain in 1 to 5 v dc
What is zone,loop/fire alarm system?
hi my name is rakesh patel i just complited my be in instrumentation & control now i am going to working as a validation engineer in a poject department so what is a scope in a future as a validation engginer ? what line is good for me can any bady give me complete solution please? your regard rakesh patel
How vortex sensor used for steam flow measurment can be checked on line i.e without taking out from process line.
hello can yoy pls send me previous papers of jindalpower and steel ltd.....'m from instrumentation..... mani1048@gmail.com
what is The specifications for oriface instalation
In bently nevada vibration monitoring system,what is the reason to maintain the Resistance of the probe + extension cable equal to 95 ohm? If possible explain the basic principle of measurement with detail electronic circuits.
HI, can anybody give details about GAS TREATMENT PLANT CONSTRUCTION,as INSTRUMENTATION ENGINEER what are the responsibilites.what are the instruments mainly instrumentation engineer will deal with
selection criteria of control valve? and selection criteria of actuator explain in brief?
What is instrumentation control?
Explain bernoulli’s theorem.
what are the definitions of input, output, command & signal according to instruments controlled by PLC using DCS System?
sir, i preparing hpcl,ongc,barc,hal exams(instrumentation engg)pls send a placement papers
Draw a wheatstone bridge circuit showing supply, meter and 3 wire RTD connection
If a warning lamp will operate with the ground circuit is bypassed with a jumper wire to ground, what should you check?