Answer Posted / subra
During the staring period The electrical equipments are taking more current example aircondion units, lifts , transformers,chillers etc
this may be 6 times of the ratedcurrent
this instantanious current is called inrushcurrent
| Is This Answer Correct ? | 1 Yes | 1 No |
Post New Answer View All Answers
i am going to correct power factor of 1600kw induction motor,when i calculate capacitance of capacitor it is three time more in star connection than delta. if motor is star connected which connection i shall adopt for capacitors and reason for adopt this connection
Name the test signals used in control system
What is the diff. between single compression and double compression gland
how to synchronize 3 phase slip ring induction motors of different ratings.
DG SET BLOCK DIGRAM
what is relay what is protection & contact multiplying relays where it is used function in brief
What should be the voltage between Neutral and Ground in secondary side of the step down transformer (230 V to 110 V) with no load condition?
I have done my m.tech in electrical engg discipline. Can any one please suggest me how should I prepare for getting into phd in iit or nit.How should I prepare for getting into lecturership
Its possible to use 3core 2R of 240 sq.mm cable for 3phases & separely 50sq.mm 3core cable fully for Neutral for connection of PCC to MCC 3ph..4wire system?
how braking & making capacity of circuit breaker is calculated?
Why using synchronising methed in DG's sets?
What is core CT & it's function?
Pl. give me checklist for installation & commissioning of machine tool.
How you will determine the volume of oil in a particular Distribution transformer.
How to calculate Number of Earthing Pits....???