How to calculate u.p.s load parsentage plz give me formula
Answer Posted / thangapattu
Befour we should note down the full load of current (rated
current value) Ex-400kva UBS =105A/630a*100
where
105A=currentValue in particular time
630A= Rated Current Value For UBS
= 16% is the percentage load Of UBS
| Is This Answer Correct ? | 4 Yes | 1 No |
Post New Answer View All Answers
What is true sine wave or pure sine wave inverter?? Is it sine wave or step wave?? If it is step wave, waves with how much step is considered as pure sine wave? Is it possible to produce pure sinewave using power electronics?
A 7 storey building has a floor area of 35,000sq.ft on each storey. On the ground floor 11KV electrical sub-station is to be erected. A load of 3kw for every 400sq.ft (p.f is 0.8) is proposed for each floor. fire pump 7.5hp, water pump 5hp, lift 2 nos, each 10hp and 20shop load of each shop is 5kw. calculate a. load each floor b. total load of building c. L.T feeders for aech floor and from transformer to main. d. distribution diagram e. capacity of sub-station/capacitor bank f. line diagram
State the points to be considered for selecting a particular type wiring.
What is different type of Electrical curve and how it protects the equipment's while up-normal situation?
Show the schematic arrangement of diesel power station layout and give its principle of operation.
testing of Vector Group – YNaoD II
What are the main faults of DC generators?
7- What is the Dissipation Factor and the difference between it and Insulation Resistance Test? 8- What is the task (function) of DC and AC reactors in power plant? 9- What is the task (function) of (open delta with earthed) in some types in transformers? 10- What is the base of the selection of the vector group in transformers? 11- What is the zig-zag transformer and its function by drawing in large detail? 12- What is the polarity ? 13- Why we make short between phase(R) in high side and phase (r) in low side in vector group test? Where High Side ( R ,S and T ) and Low Side ( r ,s and t ). 14- What are the time on delay and time off delay? 15- What is the vector group? 15- What is the task (function) of different types of vector group such as Dyn11 , Dd0 , YNd1,……..,?
What is the formula to calculate distribution transformer De-rating on iron losses basis
What is a signal flow graph?
Which level of the Transformer oil got dielectric strengh? And why?
draw the block diagram of fire alarm?
what are the necessary basic electrical topics to learn for mechanical engineer to deal practical problems.
What is the slip speed?
can i use 4 number of circuit breaker as single phase manual change over switch? if yes then how plz also send ckt diagram at nazimzamurad@gmail.com