What is the formula for calculating Transformer Losses &
Efficiency. I want to compare the Transformer efficiency at
different loading condition.
Answer Posted / s.ravi
Efficiency =
(Output/Output+Iron losses+Copper losses)*100
Iron losses = No load test,
Copper losses = Short circuit test
Regulation = (Impedance voltage/Rated input voltage)*100
Impedance voltage = Short circuit test(Voltage drop)
| Is This Answer Correct ? | 59 Yes | 33 No |
Post New Answer View All Answers
what is droop control?
What current position are you holding in your current company?
I HAVE BEEN SELECTED FOR APGENCO A.E(ELECTRICAL) 2008.HOW MUCH WEIGHTAGE FOR INTERVIEW AND WRITTEN TEST.HOW I HAVE TO PREPARE. PLEASE GIVE INFORMATION IF U KNOW.WHAT ABT G.D THIS TIME.CALL RATIO 1:2
how to find out cable size if load is 2800 watts, 230 volts AC supply and load distance is 1800 meters
What are the criteria shall be considers for sizing Fuse and MCB? If the rated current is 10Amps what should be the fuse size / MCB Size?
What is Long rod insulator and it's applications..? merits over the disc insulator ..?
we need a ntpc previous papers
what is current check gurd relay?
What is the difference between electrical earthing and electrical grounding?
Mention the difference between Analogue and Digital circuit?
what are the analog quality input for protection function?what are minimum reqiments?
We have two APFC panels in same station. I need how to connect CT in two APFC panels.can we take one CT in series connection or two separate CTs.
How to calculate the multiplying factor for energy meter with ct ratio given
how do u gauge the size of the cable ?for eg. consider a 300 sqmm L.T Cable.How do u determine the size of the cable seeing it pratically?
what is load despatching