Answer Posted / chandra
power factor gives us a measure of the energy that is stored
in the capacitors and inductors.Inductors and capacitors
doesn't dissipate energy but,they constantly gets charged
and discharged.So,the whole power transmitted by the power
company doesn't go the customers.i.e,they can't utilize the
maximum power capability of the line.
Power factor is also important in
calculating bus voltages in a load flow problem.
| Is This Answer Correct ? | 2 Yes | 0 No |
Post New Answer View All Answers
Give me the calculation steps to design an electromagnet to be work in 230V 50 Hz AC Supply. Also give force that is created by that electromagnet when it gets energized.
In the N-series schneider reclosers. What is the difference between current during fault time and current at tripping? This appears in the Event log in an event of a trip out.
In EHV transmission line a neutral grounding reactor is often placed at neutral point of shunt reactors. What is the recommended protection for this neutral grounding reactor? Should I use a fast closing switch to bypass neutral grounding reactor when this protection operates?
What is formula calculation size cable wire ?
earth also having a gravitational force (magnetic field of north and south)but it attracts any object compare to this theartifical magnetic cant perform same as earth why?
What is a commutator?
We have given to 3phase supply to ups system & how can coming netural
what is the difference between Power and Distribution transformers ?
what is ramping rate of generator
Why increase in current leads to increase in conductor temperature?
Can anyone please give me the parameters , formula needed to calculate the circuit breakers for building services.Thanks
How to calculate multiplication factor in kva example 500kva ans pls ?
what curve and rateing would you use for a three phase 0.75kw motor?
what is meant by the phrase 'static load' in case of shorting in a generator excitation system?
What is a compensator?