Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

I want to give Power supply to a house from the Feeder,
Total Load of the House is 128 KW, how to calculate cable
size for this load ?

Answer Posted / k.prakashchandra

Diversity factor can be taken as 1.5 to 2.5 depending upon
the simultaneous similar loads.You can use 4x50 sq mm copper
cable or 4x70/95 sq mm Al cable.

Is This Answer Correct ?    0 Yes 3 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

How to select the proper VSD to operate high inertial load

1714


Can you explain about pole discrepancy scheme

2159


What is method of calculating the fault current for a MDB, 50KW, 3PH, 415V, 50HZ?

2125


What will be in Mahagenco Trade Test Exam? I want to know the same.

3671


Why are iron cores in transformers made laminated?

1095


What is the function of auadag in a cro?

1103


Basic motor transformer generator

1467


How to calculate LT XLPE CABLE for 11 kv / 433 v , 1000 kva oil type transformer system?

1905


(1)Can earth and be conected together (2) what is the diferent between earth & neutral

1784


clarify types of motor operated valves and advantages

1883


in the directional overcurrent and earthfault protection,normally we are setting the angle 45 deg lead for phase fault overcurrent and -45 deg lead for earthfault fro forward direction.but both the fault are operating on the same angle region only.why?how the relay will response?

1813


How to calculate Voltage regulation of 22 KV Over head Line.

1639


How to select the gauge of wire for winding of motors? How to select number of turns for winding of three phase induction motor?

2727


what is the current setting for different relay protection for transformer .

2281


WHAT HAPPENED DC SERIES MOTOR FIELD WINDING OPEN. CAN POSSIBLE.

3874