Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

what is field flash

Answer Posted / k.prakashchandra

Static exciter uses thyristors for converting AC to
DC .Thyristers require a minimum voltage to conduct,for
which the voltage created by residual magnetism is not
sufficient.To bring the generator volage to the required
value ,field flashing is done with dc source or AC through
rectifier.Once the required voltage is built up,the
generator output will take over the excitation with field
flashing off

Is This Answer Correct ?    1 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

What must be the minimum distance maintained between 2 Generators as per International standards?

2130


how to calculate earth fault relay current and CBCT ratio

8332


Why squirrel cage motor can only use with low starting loads ?

2047


how wecalculate breaking capcity of acb mcb mccb .explain with example

1935


what is difference between 5A and 100A CT constructional wise and operation?

3560


We have 750KVA DG set, we want to introduce REF relay with 1250/1A,CL PS,Current transformers.The lead distance of 2.5mm copper flexible cable from CT to relay is around 5mtrs.We would like to know the knee point votage(VK) & IM calculion for CT's

1915


I am having a 42KW 3 phase electrical heating furnace, heating element is 80/20 nichrome material, my connections is made in such a way that 2 star connection compromising 2 coils per phase so totally 12 coils, shall if i use it unbalanced star condition (instead of 2 group of 3 phase or 1 group of 3 phase, connecting 4 phases of 5 phases) what will be the consequences and is it acceptable?

1674


From what on-site components does the HT panel monitoring the bus-bars in a 11kV system take inputs?

2003


1- XC and the RC time constant are both measures of the reaction of C to a change in ____? 2-The power factor is a numerical ratio with a value between 0 and 1 equal to the ______________ of the phase angle. 3-When V and I are out of phase because of reactance, the product of V times I is called ______________ power 4-For _____________ inductors, the branch currents can be added algebraically. 5- The ______________ power in watts can be calculated as I^2R 6-Calculate XL with L = 30mH and f = 1kHz ( I have Xl=2piFL 2*3.141592653*1kHz*30mH =188 ohms Please check) 7-A parallel RL circuit has the values, R = 5kohms, XL = 5kohms. A voltage source of Vt = 10Vrms is connected in parallel to R and L. Determine the total current, It delivered by the voltage source Vt. 8-A series RC circuit has R = 1Mohm and C = 1microF. How long would it take for the capacitor to fully discharge if it is initially fully charged? 9-A circuit has real power = 300W and an apparent power of 500VA. Determine the power factor and phase angle. 10-The time constant for an LR series circuit is T = 0.1s and R = 10ohms. Calculate the inductance L.

3367


What are the factors influence the choice of an electrc drive?

2076


how to calculate the formula of cable size if motor kw is given

2265


Define characteristics impedance?

1121


Define maximum demand?

1055


how was your last weekend.

1786


I need HT sphere gap calibration table. Can any body help me.